Are 100A & 225A frame sizes the same or does the 225A frame require more space?

I do not think there are any standards for frame sizes between manufacturers.

A manufacturer could potentially make them the same size. They could even make one model the same size and a different model a different size.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Are 100A & 225A frame sizes the same or does the 225A frame require more space?

not usually
generally yes

Highly recommend you look at an SQD catalog and an ABB catalog - they will even have dimentions. That's better than anything we could tell you.

ice
 

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
The simple answer, if 100a an 225a trip units have the same dimensions accordingly the frame sizes will be.
 

templdl

Senior Member
Location
Wisconsin
Are 100A & 225A frame sizes the same or does the 225A frame require more space?

It has been my experience to be suspicious of what the test of the story is. The history of the sdize of MCCBs has evolved over the years. If you are referring to vintage breakers the 225a breaker often is the same width as a 100/150a breaker but longer. Then the 225 evolved into a 250.
Then 100/150a (f-frame) frame was able to be reengineered to be up to 225a.
But, caution must be used because if your intent is to replace an f-frame 150a breaker with a 225a f-frame as the panel may not be listed for the 225a f-frame.
As such simply saying that the "f-frame" may now be available up to 225a may lead to an incorrect application without knowing what you are intending to do.
 