mbrooke
Batteries Included
- United States
- Technician
In a delta wye 480 to 208Y/120 volt transformer, what is the maximum length the secondary feeders are allowed to travel?
If your primary OCPD is sized at 125% or less, you don't need secondary OCPD at all.
Is that what you're asking? How far can the secondary conductors travel before you need OCPD?
If your primary is sized at 125% of less, you don't need secondary protection for the Transformer. The secondary conductors will still need protection, requiring an OCPD.
Section 240.21(C) gives the maximum secondary conductor length for several different installation situations.
Noted and addressed in Post #3
That is incorrect.I know for a fact that is incorrect. The 125% primary rule applies only to a delta delta or a 2 wire to 2 wire.
Delta wye as is the case (as well as delta detla center tap or single phase 120/240) needs secondary protection no matter what.
The issue here is a how long the secondary conductors can travel to the panel board and under what conditions.
In answer to your OP:
"In a delta wye 480 to 208Y/120 volt transformer, what is the maximum length the secondary feeders are allowed to travel?"
the maximum length is infinite...... per 240.21(C)(4)
Ok Im starting to make sense of it.
Just confused why parts of the code say a secondary breaker is needed while others let it go...
I think people get confused on the fact that the Transformer Protection and the Conductor Protection are separate items (probably because one OCPD most often provides both functions.)
You can have a transformer that has "Primary Only Protection" but still need an OCPD on the secondary side to protect the secondary conductors. In this case, the secondary OCPD will not be providing Transformer Protection as far as the Code is concerned, only the secondary conductor protection.
Happens a lot.. that's why they added a reference note in Art 450 to Art 240 for conductor protection.Ok its beginning to make sense. Im getting the two mixed up as one concept.
Thanks!![]()