jaggedben
- Northern California
- Solar and Energy Storage Installer
No on the 35 amp breaker. You have to size your OC protection at 125%...in your case...34.375x125%= 42.96amps...so 45amp BKR
We are telling you that you can load side connect your system to the 200 amp panel because under the 2014 code your allowed to use the actual system output for the 120% load side calculation...not the size of the circuit breaker as required in previous code cycles.
The OP had the math correct.
And it's 125% of the rated (not actual) system output that goes into the 120% rule, so he still cannot connect load side.