Sparky2791
- Northeast, PA
- Electrical Design
I am working on a project with an electrical contractor to install an outdoor generator docking station. Plans are to intercept the incoming underground feeders from the utility transformer and reroute them into the docking station which will be service entrance rated and have both a service entrance circuit breaker and a generator circuit breaker with a kirk key lock between them. Since the service entrance circuit breaker will now be located outside in the docking station remote from where the current grounding electrode system is located (inside the building) and because you should only bond the neutral to ground once in the system I have a few questions;
I am having confirmed if a ground wire is currently installed in the existing service entrance feeders and what size it is.
Thank you for your time.
- Should the neutral to ground bonding jumper be removed from the existing grounding electrode system (GES) inside the building currently?
- What should the ground wire from the docking station to the existing GES in the building be sized on (250.66 or 250.122). This seems to be a bonding jumper so 250.122 however it is after the neutral to ground bond was made so is it an equipment ground now and 250.66 rules?
- Is it necessary to drive a ground rod @ the docking station?