I am being told I need an insulated ground feeding my sub-panel which feeds a pool panel. I have an insulated ground from the sub-panel to my pool panel. Why am I being told the sub-panel needs one? Code states:
680.25 (B) Grounding:
An equipment grounding conductor shall be installed with the feeder conductors between the grounding terminal of the pool equipment panelboard (which in my case is the pool panel) and the grounding terminal of the applicable service equipment (which in my case is the sub-panel) or source of a separately derived system?.this equipment grounding conductor shall be insulated.
Any thoughts?
680.25 (B) Grounding:
An equipment grounding conductor shall be installed with the feeder conductors between the grounding terminal of the pool equipment panelboard (which in my case is the pool panel) and the grounding terminal of the applicable service equipment (which in my case is the sub-panel) or source of a separately derived system?.this equipment grounding conductor shall be insulated.