Might be doing some grid PV in the near future so trying to get up to speed....what do I have correct:
1) In general I can choose to have the DC system grounded or ungrounded if I meet their respective requirements.
2) Where over-current protection is required such as where strings are paralleled, if the system is grounded I only need a fuse in the ungrounded conductor. If the system is ungrounded I need a fuse in both conductors.
3) A transformerless inverter will automatically make the DC system grounded because there is no isolation from the utility system (assuming grounded utility system)
4) Does going DC grounded/ungrounded require coordination with the inverter used?
5) Im a little confused: What is the difference in ground fault detection required by 690.5 and 690.35(C)? Why not just reword 690.5 to read "grounded and ungrounded....."
Thanks!