Main breaker/main lug sub panels
A sub panel does not need one.:thumbsup:
Well that depends!:)
Never say never!:p
Remote structure more than 6 handles
:thumbsup:
To add to these answers:
True you don't have to install a main breaker. But sometimes you do have to have a disconnect which could be a breaker or fused disconnect.
Basically, if the subpanel is not in/on the same building as it is being fed from, you need a means to disconnect all the ungrounded conductors if there is more than 6 handles (breakers) or 6 "throws of the hand".
Never say never!:p
:thumbsup:
Right, That's what I thought. I'm far from a code book guru and I generally go with what I was taught (along with trying to keep up with changes each cycle). Thanks.
I am still going with a main breaker is never required in a panel. It is a design choice.
A disconnecting means for a remote structure or building is required but how that is accomplished is also a design choice.
that would appear to be THE answer.
Are you saying a remote structure (shed) needs a means of disconnect at the remote structure no matter how many handles?
Running 30 amp 240volt to shed. Looking at using main lug panel. Will only put 2 circuits off of said panel. Disconnect located at shed required? Or is the 30 amp DP breaker in garage supplying said panel sufficient?
If only 2 circuits then you are good. You need a 4W feeder and a GES at shed.
If you are under the 2011 or earlier code, the second building disconnect must be suitable for use as service equipment. Some panels are only so listed where a main breaker is installed in the panel.
When are we required to install a main breaker in a sub panel as opposed to using a main lug panel?
The question is not specific enough to rule it out so here goes.....don't forget a sub panel supplied by a transformer will usually need one. Yes not required to be in that panel but typically how it would be done. Wait, maybe that wouldn't be a sub-panel, let me grab my NEC and look up the definition of "sub panel" ;)
Ooo ooo ooo.... just thought of another one: A panel supplied by a tap. And yet another one: when the main breaker panel is cheaper than the main lug version, as the case with those 100A MB homeline value packs ;)