how can I feed two panels off secondary of 75k, 480-120/208v. Transformer

pnl-1 ihas 100a mcb and pnl-2 has 70 a mcb

pnl-1 is in south of the buildg and pnl-2 is in north

tanx
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You can. Just keep the transformer secondary rules in 240.21(C) in mind.
 

Smart $

Esteemed Member
Location
Ohio
You can. Just keep the transformer secondary rules in 240.21(C) in mind.
And if those rules do not permit the distance you have to the panels, you can get around that by installing fused disconnects, or MCCB's in an enclosure, within the specified distance.
 