Homeline 40/80 panel

Status
Not open for further replies.

nizak

Senior Member
Has anyone here been using Sq D Home line 200amp 40/80 panels?
The two that I recently installed seem to have "slop" in the bus attachment to the breaker.I'm noticing it when I plug the breakers in they seem to want to drop a bit. It appears the jaw connection is ok just not as tight as the conventional 40 space.Once the cover is installed everything looks OK.
 
Ive seen 'em at the SH. They said they havent sold ANY yet! I wouldnt be against trying one out, but with all the AFCI breaker requirements, seems like it would be a big waste, since you really are limited to what you can use tandems on.
 
Haven't used one yet. Murry has had one for some time now. Seems like it might be good for a service upgrade where the HO has numerous and existing double and triple tapped breakers.
 
Ive seen 'em at the SH. They said they havent sold ANY yet! I wouldnt be against trying one out, but with all the AFCI breaker requirements, seems like it would be a big waste, since you really are limited to what you can use tandems on.
My thoughts as well - you would seldom get more then 40 spaces out of it in dwelling applications anyway.
 
My thoughts as well - you would seldom get more then 40 spaces out of it in dwelling applications anyway.
Maybe so, but I just upgraded a 100 amp service to 150 thinking I had enough spaces in a 30 circuit panel. Surprisingly, I just made it. When I opened the existing panel they had numerous piggy-backed breakers double tapped. And this was basically a bungalow on a small piece of property. The existing main breaker had corroded and burnt up because a couple of hacks decided to add sub-panels for an electric dryer and an AC unit, tapped off the main lugs with copper wire to aluminum triplex and no anti-oxident. Go figure.
 
Maybe so, but I just upgraded a 100 amp service to 150 thinking I had enough spaces in a 30 circuit panel. Surprisingly, I just made it. When I opened the existing panel they had numerous piggy-backed breakers double tapped. And this was basically a bungalow on a small piece of property. The existing main breaker had corroded and burnt up because a couple of hacks decided to add sub-panels for an electric dryer and an AC unit, tapped off the main lugs with copper wire to aluminum triplex and no anti-oxident. Go figure.
Too much load should trip that main that is one of it's primary purposes - overcurrent protection. If it is corroded there is some other issue causing corrosion.
 
Too much load should trip that main that is one of it's primary purposes - overcurrent protection. If it is corroded there is some other issue causing corrosion.
Granted. I believe the issue (in my case) was copper wire being tapped onto the aluminum SE cable at the line side lugs with no anti-oxident (primarily because they didn't want to pay an electrician to upgrade the service).

BTW, I didn't want to pirate this thread away from the OP. Using a 40/80 panel would be OK if the circuits were predominantly lighting and receptacle loads, IMHO.
 
Granted. I believe the issue (in my case) was copper wire being tapped onto the aluminum SE cable at the line side lugs with no anti-oxident (primarily because they didn't want to pay an electrician to upgrade the service).

BTW, I didn't want to pirate this thread away from the OP. Using a 40/80 panel would be OK if the circuits were predominantly lighting and receptacle loads, IMHO.
Now bring in 2014 AFCI/GFCI requirements and find us some tandem sized AFCI/GFCI breakers so we can use all 80 potential spaces. Most dwellings using this panel and wired with 2014 NEC will only be able to take advantage of just a half dozen spaces at the most that could utilize tandem breakers, so a 30/40 panel would work just as well and those have been around for some time.
 