david
- Pennsylvania
I did a final inspection fir a dental office. I removed a panel cover and found the neutral in the panel not landed along with a red conductor. The red conductor because they ran out of 12/2 and the red conductor wasn't used at all. At first I didn?t think much of it. I already asked if any multi-wire circuits where run for any of the branch circuits and was told no.
Then I asked what is this neutral for did you run any spare circuits. The answer was no spare circuits.
And the electrician also stated everything is working.
As most of you already figured out if the circuit is working and the neutral is not landed then something is wrong. The electrician then landed the neutral for the circuit then got a little ticked when I said you need to trouble shoot that circuit he said why everything is working.
I asked if he had an amp meter and I had them run a small shop vac. On the circuit 2.4 amps on the ungrounded and .4 amps on the grounded conductor. He was still agitated so I ask if he had a spare ark fault breaker in his van he said yes, and used it for a test on the circuit to my surprise the circuit held. I then said it may have been a poor choice on my part to suggest an ark fault breaker for this test I then suggested a GFCI circuit breaker when the GFCI opened the circuit I was then able to convince him it was important enough to trouble shoot the circuit. It turned out that an equipment ground was pushed up against a neutral in one of the hall rec. outlets.