vhoa
- Fremont CA, USA
Is it against NEC code for installing a 480V , 3 phases -Fused disconnect switch inside a pullbox?
I cannot think of a fused disconnect that COULD be mounted in a pull box anyway. Or are you thinking of using one of those cheap little UL508 rated rotary through-the-door type? If so, are you using it correctly? There are some restrictions to using those, the kind the salesmen never tell you about...
This might turn out to be a more immediate problem before you even get to the fused disconnect part. Where is this concept coming from? Is there a PE involved?The Fused Disconnect used in our design is only to limit available fault current to our existing 480V panelboard, which is rated at 10KAIC and has no main breaker. The panelboard is fed from a 200A feeder breaker in our switchgear lineup in the next room. The fused disconnect is NOT to be used as a disconnecting mean.
Where is the pull box physically installed in the circuit? Are you talking an underground pullbox? A pullbox in an electrical room next to the panelboard? On a wall outside?
Agreed. If you are using the current limiting curves from the fuse manufacturer without having actual series ratings for all of the downstream combinations of equipment, it might be a non-starter.
Other than very particular criteria, you cannot consider the CLF limiting the fault current . You need an actual tested combination (series rating)I accidentally left out the rating of the 480 V panel is 10kAIC in the background info in the response to Jraef's comment. the CLF limits the fault current to about 4 kAIC.
so what I want to know is "Can we install overcurrent protection device inside the above ground pull box if all clearances are met?"