Is it legal to feed a 112.50 KVA transformer with 480 volt power using a 150 amp breaker (primary) and then come out to a 120/208 panel that has a 125 amp main (secondary)?
Is it legal to feed a 112.50 KVA transformer with 480 volt power using a 150 amp breaker (primary) and then come out to a 120/208 panel that has a 125 amp main (secondary)?
Is it legal to feed a 112.50 KVA transformer with 480 volt power using a 150 amp breaker (primary) and then come out to a 120/208 panel that has a 125 amp main (secondary)?
As others posted, sure it's legal. I recommend reading 450.3 and table 450.3B.
Keep in mind that just because it is legal, doesn't mean it will work. Don't feed bad if you get nuisance trips.
ice