408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor
Each "opening" is considered an individual terminal. Listing of the block will tell you if each opening is intended for single or multiple conductors, and what size of conductor(s) is acceptable.is a "terminal block" considered "an individual terminal"? all bare's in my service panel are on this single/dedicated terminal block, but some of the screws on that TB are squishing two bare's. i guess next Q is, why is having two a bad thing?
And when a terminal is designed for two conductors they often are designed only for two of the same size so there will be even amount of pressure applied to both conductors. If you placed a 12 solid and a 14 solid in same termination there is greater chance of less pressure being applied to the 14 especially in most set screw type devices with no other type of pressure plate or other clamping method and it may develop continuity problems because of this.The main reason in having two, without proper design support, is the risk that either one wire will not be as tightly held as the other or that relative movement if the two wires might loosen them both.
The hazards of loose connections are well known, so I will not go into them.
408.41 in the 2014 Nec
Also in the 2011
In most cases, the neutral conductor is a grounded conductor. For the cases where the neutral conductor is not a grounded conductor, that section would not apply.And what if it is a?:
Neutral Conductor. The conductor connected to the neutral
point of a system that is intended to carry current under
normal conditions.
I recall there being a fairly lengthy thread about screw terminals on devices, receptacles I believe, but perhaps others, such as wall [snap] switches. Can't remember the consensus... perhaps someone will find it and provide a link...If I put more then 1 wire under a terminal I use ring terminal crimps, and sometimes star washers too. Spades or forks will squeeze out.
But it depends on what kind of terminal you are talking about. But this is new to me I hadn't considered the rules about this one.
Anyone know exactly how they put the screws described in here in such items? They can't really be thread forming screws as that would tap the hole and they would thread back out easily, they are somehow designed and installed in a way that they can not easily be backed all the way out the hole yet need to be inserted in the hole the first time somewhow.I recall there being a fairly lengthy thread about screw terminals on devices, receptacles I believe, but perhaps others, such as wall [snap] switches. Can't remember the consensus... perhaps someone will find it and provide a link...
Anyway, doing what you describe on screw terminals of typical yoke mounted devices is not a violation that I know of. But I think using ring terminals should be avoided on these. My reasoning is the manufacture process nowadays uses thread forming screws to make the threads in the mating back-plate contact. When you back the screw all the way out to put on one or more ring terminals, you remove a little more of the back-plate thread mass. There's little there to begin with. Then you remove a little more putting the screw back in. This degrades the thread to the point where adequate compression torque may not be possible. You also create filings in the device that may aid in the formation of an arc fault. The preceding isn't a substantially significant reason to not do it, but I believe something to consider before doing it (or doing it again).
I would think they have to distort them somehow after installation otherwise they would back out easier then they do. Many times when you do fully remove such a screw it no longer has that resistance that keeps it from easily backing out.I believe that the end threads are either pre-distorted or are distorted after they are threaded in.