I need to install a Wall Connector for a Tesla which is rated at 240V/80A. This will be installed on the wall in a vehicle bay (i.e., executive garage area) inside a commercial building.
According to the 2011 NEC (adopted in California), a locking disconnecting means must be installed.
What is not clear to me is, what is considered a "readily accessible location"? While this vehicle bay is not a showroom, for esthetic purposes I would prefer to not place a disconnect on the wall next to the charger. Does "readily accessible" mean within line-of-sight? Or can the disconnect be in another room? Also, is there a maximum distance that would still be considered "readily accessible"?
Seems like this term should be defined in Article 100.
625.23 Disconnecting Means
For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker used as the disconnecting means and shall remain in place with or without the lock installed. Portable means for adding a lock to the switch or circuit breaker shall not be permitted.