Michaelmechanic
- Ft lauderdale fl Lu 728
How do you know how much amperage is available on the utility's wires to a house? For an upgrade of service
It is really nothing to worry about assuming you are notifying the power company about the up grade which I bet is required by the power company's terms of service that the customer has to agree to.
In my area a utility is supposed to be involved with a service upgrade so it is up to them to upgrade the conductors if they think it is needed. They are unlikely to upgrade.
I once rewired a 30 unit, 5 story apartment building. When we started every unit had one 14 AWG circuit running to it with 30 amp fuses supplied by a 100 or 200 amp 3 phase service. When we were done it had an 800 amp 3 phase service and 60 amp feeders to each unit.
The power company did not change the underground wire. When I asked them about it they said something that made a ton of sense. What load did I add to the service? In truth the connected load would be the same. The power company knew what this building should take to run and the NECs load calculations have nothing to do with it.
Doing an addition on the house and my main being a 100a . I want to go to 150a or 200a. Why would the utility need to be notified if their wire was already sufficient.
I was just curious if there was a way to figure out how many amps was available
Available? Depending on conditions, there might be 1000 amps available, but not for very long :lol:. You could trace the service conductors back to the transformer and see how big that is.
As others have said, electric service is usually a "tell us what you think you need and we'll put in what we think you need".
(z remembers the back and forth with PEPCo about refurb-ing a 1923 theater... going from maybe a 400a 3phase service to IIRC a 2000a one. Fortunately, I was not the one doing the load letters on this.)
That is hard for most people to put their heads around. Read the green.
In Florida, they size the secondaries to the NEC and the POCO has nothing to do with them. I have a job right now where the Transformer puts out a maximum of 2776 amps. The calculated load is 4250 amps. The Engineer is requiring 8 sets of 750 MCM copper to feed the customer tap box, which I pointed out to the EE was rated at only 3800 amps. They of course, said it was OK, but didn't reduce the individual secondaries in size. What a waste of money and metal.
I can't make a bit of sense of that.![]()
Around here we do the service upgrade with a permit from the town and don't tell the POCO unless we're moving the service, the drop, need a lock removed, etc. After the local inspection the EI sends a cut-in card to the POCO and then they come out to inspect, possibly change the meter and install permanent connections. If the drop requires changing they will do that too.
I'm having some trouble making sense of it as well, but I'm guessing you are saying the owner side of things needs sized per NEC and the POCO side of things is often (maybe always) smaller. The calculated load you mention of 4250 is probably NEC calculated load, and anything on owner side of service point is probably sized according to that value. POCO's will run equipment at higher limits then NEC, but one must also remember their equipment is outdoors and is not going to burn down a building if overloaded for too long. They also take other factors into consideration sometimes, like how long the maximum load will be present, how long will equipment be at a minimal load where it can cool, time of day and/or average temperature during peak demand periods as well. Overhead conductors will be smaller then underground conductors supplying an identical load, but they are in free air to dissipate some heat.In Florida, they size the secondaries to the NEC and the POCO has nothing to do with them. I have a job right now where the Transformer puts out a maximum of 2776 amps. The calculated load is 4250 amps. The Engineer is requiring 8 sets of 750 MCM copper to feed the customer tap box, which I pointed out to the EE was rated at only 3800 amps. They of course, said it was OK, but didn't reduce the individual secondaries in size. What a waste of money and metal.