M mjc1060 Senior Member Sep 24, 2014 #1 Hi, Does the NEC restrict mixing 120V (receptacle) circuits with 277V (lighting) in the same conduit?:?
Hi, Does the NEC restrict mixing 120V (receptacle) circuits with 277V (lighting) in the same conduit?:?
iwire Moderator Staff member Location Massachusetts Sep 24, 2014 #2 mjc1060 said: Hi, Does the NEC restrict mixing 120V (receptacle) circuits with 277V (lighting) in the same conduit?:? Click to expand... Nope, they just need to be identified.
mjc1060 said: Hi, Does the NEC restrict mixing 120V (receptacle) circuits with 277V (lighting) in the same conduit?:? Click to expand... Nope, they just need to be identified.
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Sep 24, 2014 #3 iwire said: Nope, they just need to be identified. Click to expand... But be careful if they feed devices (receptacle and switch, for example) in the same box.
iwire said: Nope, they just need to be identified. Click to expand... But be careful if they feed devices (receptacle and switch, for example) in the same box.
M mjc1060 Senior Member Sep 24, 2014 #4 Thank you the 277V light switchs and the 120V receptacles are in different boxes.