| Vd = Voltage drop |
| I = Current in amperes |
| R = Conductive resistance in ohms/ 1000 ft. |
| V = System Voltage in volts |
| Cos ? = Power Factor |
| X = Conductor inductive reactance in ohms/1000 ft. |
| L = One way length of circuit ( source to load) in thousands of feet. |
| N = No of cable runs per circuit. |
| ? = Phase angle of load |
NEC does not deal with voltage drop [except the informational note no.2 in art.215.2
Thank you, jumper.However,I meant this only for usually motor operation.:happyno:
You might want to look at articles 647 Sensitive electronic equipment and 695 Fire pumps.
Always been my understanding as well, but does not agree with this information:But as your PF gets worse, it is BECAUSE your actual load is dropping, which means LESS current to begin with, hence LESS voltage drop.
Your power factor will vary by load. For a 75 HP TECO Westinghouse motor:
50% load => 75.5 % P.F.
75% load => 83.5 % P.F.
100% load => 86.5 % P.F.
Now all we need is cable reactance.
OK to just use VD = 2*.866*Z*L*I ?
Z from NEC chapter 9, table 9
Fair point and ought to be taken into account.Ok you are on to something here, but I think we need to factor in motor efficiency as well. If a motor is 93% efficient - that is efficiency at full load, rated voltage and frequency being applied. What is efficiency for same motor if load is changed to 50%?
That is a better illustration of the point I was trying to make earlier.Originally Posted by JonD View Post
Still, not likely significant as it relates to voltage drop and cable sizing. The worst case motor efficiency I have ever seen, a 12 pole motor built in 1913 (bullet proof, but nobody worried about efficiency then), was 65% eff. at half load. So even if we apply that somewhat extreme value to Besoeker's numbers above, 37kVA /.65 = 57kVA. Cable size (if done properly) is not going to be affected.Fair point and ought to be taken into account.
Agreed.Still, not likely significant as it relates to voltage drop and cable sizing.