I have a 20,000W 460V 3Phase Delta heater load. I am trying to calculate the resistance.
I-Line = 20000W/460V/Sqrt3 = 25.1A
I-Phase = 25.1/Sqrt3 = 14.5A
R-Phase = 460/14.5 = 31.7 Ohms
What I am actually measuring with my Fluke is approximately 19 Ohms.
If I take 460VAC divided by the line current (25.1A) I do get 18.3 Ohms. Is my original calculation wrong? I definitely though I had to divide a second time by the square root of three to get the phase current, and then calculate phase resistance from there. Is that wrong, or is there something wrong with my readings. The readings are all the same from each leg to each leg as well, so I am thinking the reading is correct.