And it is 408.36 exception 1 that makes them non-compliant , correct?
(if it was installed today)
Exception 3 states existing panels are OK?
So, it's dangerous, but not THAT dangerous?
Or like falling off a ladder. The falling parts not that bad, the landing part on the other hand.......:roll:
Kind of off topic some but in general it is not acceptable.I saw a challenger panel yesterday with no breaker for the outside compressor and only a disconnect on the outside wall made by square D. Is this something anyone else has seen and is it ok to not have a breaker in the panel for the a/c unit
Are they inherently dangerous?
I cannot see the logic in answering in the affirmative. Look forward to hearing this.
Panel must be listed for it. Most "load center" panels are not. Get into commercial/industrial panels - especially the I-line panel and they often are listed for it.FWIW the 6 throw rule is stilled allowed, just not in the same panel.