This question is about grounding and bonding only with all other electrical issues (are there are some) aside.
Two connected buildings each with their own service. One is a hospital and the other is an apartment building. There is a fire wall. Sometime in the 70?s (this is when the apartment building was renovated for apartments) a transfer switch was installed in the apartment building to serve an elevator and emergency lighting. It is normally connected to the apartment building service. The standby side is connected to a feeder which is connected to a distribution panelboard in the hospital which in turn is connected to a transfer switch in the hospital. So the apartment building transfer switch standby side feeder is live.
The neutrals are all connected in the apartment transfer switch.
1. Should the standby side neutral (from the hospital) not be connected to the apartment neutral?
The way to do this is a 4 pole transfer switch? (It is currently a 3 pole transfer switch.)
Maybe when they installed it they considered it one building because there is no disconnect on the standby feeder where it enters the apartment building (the disconnect is the circuit breaker in the hospital panelboard).
2. If we say it is two buildings and add a disconnect on this feeder at the wall of the apartment building (calling is a service entrance ? emergency/standby whatever) should the neutral be bonded to a ground at that point?
Two connected buildings each with their own service. One is a hospital and the other is an apartment building. There is a fire wall. Sometime in the 70?s (this is when the apartment building was renovated for apartments) a transfer switch was installed in the apartment building to serve an elevator and emergency lighting. It is normally connected to the apartment building service. The standby side is connected to a feeder which is connected to a distribution panelboard in the hospital which in turn is connected to a transfer switch in the hospital. So the apartment building transfer switch standby side feeder is live.
The neutrals are all connected in the apartment transfer switch.
1. Should the standby side neutral (from the hospital) not be connected to the apartment neutral?
The way to do this is a 4 pole transfer switch? (It is currently a 3 pole transfer switch.)
Maybe when they installed it they considered it one building because there is no disconnect on the standby feeder where it enters the apartment building (the disconnect is the circuit breaker in the hospital panelboard).
2. If we say it is two buildings and add a disconnect on this feeder at the wall of the apartment building (calling is a service entrance ? emergency/standby whatever) should the neutral be bonded to a ground at that point?