690.64 Point of Connection.
Commentary Note
The supply-side connection is similar to installing a second service entrance, and the numerous requirements of Article 230 apply.
There is a 200 amp panel mounted on the outside of the dwelling next to the utility meter, with a 200 amp main. One 30 amp 2-pole and one 100 amp 2- pole.
The 200 amp breaker is feed from taps to service entrance conductors on the load side of the utility meter.
30 amp 2 pole from the PV system from the array mounted on the house back feeds the bus(200 amp exterior panel)
There is a 100 amp panel at the garage back feed by a 30 amp 2-pole breaker from the PV array at the garage.
. A 100 amp 2 pole Main at the garage panel back feeds the 100 amp 2-pole in the panel on the exterior of the house.
Since the 200 amp exterior panel at the house was installed by the PV contractor he says this is not a service panel it?s a PV panel and none of the rules in 230 apply.
My question is should this 200 amp panel be considered a service disconnect and is it required to be grouped with the service disconnect in the basement of the house
Commentary Note
The supply-side connection is similar to installing a second service entrance, and the numerous requirements of Article 230 apply.
There is a 200 amp panel mounted on the outside of the dwelling next to the utility meter, with a 200 amp main. One 30 amp 2-pole and one 100 amp 2- pole.
The 200 amp breaker is feed from taps to service entrance conductors on the load side of the utility meter.
30 amp 2 pole from the PV system from the array mounted on the house back feeds the bus(200 amp exterior panel)
There is a 100 amp panel at the garage back feed by a 30 amp 2-pole breaker from the PV array at the garage.
. A 100 amp 2 pole Main at the garage panel back feeds the 100 amp 2-pole in the panel on the exterior of the house.
Since the 200 amp exterior panel at the house was installed by the PV contractor he says this is not a service panel it?s a PV panel and none of the rules in 230 apply.
My question is should this 200 amp panel be considered a service disconnect and is it required to be grouped with the service disconnect in the basement of the house
Last edited: