220 residental dishwasher

Status
Not open for further replies.

JDB3

Senior Member
I am currently working on a residential plan that indicates a 220 volt dishwasher. :huh:
If indeed it is a 220 volt dishwasher, by the 2014 NEC, will it be required to be GFCI protected ?? :?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
That would not make any difference. The 2014 article 210.8(D) says that GFCI protection is required for outlets that supply dishwashers in dwelling units. In this context, "outlet" would mean either a hard-wired connection in an outlet box or a receptacle outlet.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
I am currently working on a residential plan that indicates a 220 volt dishwasher. :huh:
If indeed it is a 220 volt dishwasher, by the 2014 NEC, will it be required to be GFCI protected ?? :?

Is it "220V"? Or that just oldtimer speak for "240V"?

Cause if it is "220V", then: Is it also 50Hz?

edit to add: Not an answer to your question - just curiousity

ice
 

JDB3

Senior Member
Often times people still use 220V for 240V just as they still say 110V for 120V
Yes sir, just like the voltage around here runs from 125 to 129. So, just easier to keep it 110.
Also like a 44 Mag. round, is not, a true 44, but .429. Therefore 44 easier to say. :D
 
Last edited by a moderator:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I've only seen a few residential dishwashers that were "220" and they were indeed 50 Hz.
 