I was wondering why ovens even have neutral wire connection? electronics and blower? then on neutral should not be more than 0.5A but per NEC it has to be counted as CCC. Heating elements are off 208V and without connection to neutral probably.
Here's some examples of when to count the neutral as a CCC:
208Y/120 volt system-different circuit types:
A)- 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B)- 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C)- 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*
Notes:
A)- A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
B)- In this circuit the neutral current will be nearly equal to the current in the ungrounded conductors so the neutral counts as a CCC
C)- In this circuit the neutral will only carry the imbalance of the current between the three ungrounded conductors so it is not counted as a CCC, with one exception, *if the current is more than 50% nonlinear then the neutral would count as a CCC.
120/240 volt system-different circuit types:
D)- 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E)- 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Notes:
D)- A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
E)- In this circuit the neutral will only carry the imbalance between the two ungrounded conductors so the neutral is not counted as a CCC.
| dura lex sed lex | [the] law [is] harsh, but [it is the] law | |
Correct, on a 208/120 system it is not imbalanced current unless all three phases are part of the circuit. However the neutral conductor doesn't necessarily need be same size as ungrounded conductors if it is not going to see the load - but I believe there is a 70% rule that may kick in for a range.Te above is true but none of the conditions are met by my oven circuit. Neutral in my circuit does not carry the imbalance but rather actual small load of electronics, blower and bulb(s) so it has to counted per nec as CCC.
It's silly cause this 0.5A on neutral ruins my derating.
dura lex sed lex [the] law [is] harsh, but [it is the] law
If I have 4 electric ovens fed with 2 hots and 1 neutral each from 3 phase 208 V wye system how many CCCs do I have in one conduit? 8 or 12?
IMO you have 12 current carrying conductor's based on 310.15(B)(5)(b)
(b) In a 3-wire circuit consisting of two phase conductors
and the neutral conductor of a 4-wire, 3-phase, wyeconnected
system, a common conductor carries approximately
the same current as the line-to-neutral load currents
of the other conductors and shall be counted when applying
the provisions of 310.15(B)(3)(a).
Agreed. But that does not mean that all three conductors will have the same, large current. Please see the attached sketch.Your oven circuits are shown as (B) above. You have 3 CCCs per circuit.
Nice jumper I was looking through my phone for the same one I was given as well to post. That one post really helped ne understand how to visualize it.This is a copy of a post written by Rob/Infinity that explains when a neutral is counted as a CCC.
Of coarse I have the same one. ..thanx rob/infinity . No matter how it applied to this thread its good infoThe thanks/credit really goes to Rob/Infinity, he wrote it. I merely copied it and reposted it.