jxofaltrds
Retired ESI
- Mike P. Columbus Ohio
- Creator
Most of the local inspectors require all the equipment grounding conductors (EGCs) in a box to be connected regardless of their wire size or ?association.? For example, consider a two-gang box in a kitchen with a small appliance branch circuit and a lighting circuit. Some say it is because of ?equipotential? issues. However, the heading of this section in part references the ?Continuity ... of Equipment Grounding Conductors.? In the body of this section, it states, ?any EGC(s) associated with those circuit conductors shall be connected.? How are these two circuits associated? If the inspectors are correct, why does the NEC not state, ?all EGCs in the box shall be connected together??
I was taught this way but after discussing this at last nights IAEI meeting I am questioning if we are required to tie EGC of different branch circuits together, specially in a NM box.
Thoughts?
http://www.ecmag.com/section/codes-standards/outside-feeders-egcs-and-more
250.148 Continuity and Attachment of Equipment
Grounding Conductors to Boxes. Where circuit conductors
are spliced within a box, or terminated on equipment
within or supported by a box, any equipment grounding conductor(
within the box or to the box with devices suitable for
the use in accordance with 250.148(A) through (E).
Thoughts?