SPARKY1953
New member
- NH
I have house that receives it's service from a detached garage. The main 200 amp service starts at the garage goes through a 200 amp 120/240 disconnect is piped in pvc underground to the house with 3 4/0 xhhw to a 200 amp main breaker panel in the house the neutrals and grounds have been separated in the main panel and a #4 copper run from the equipment ground bar to 2 driven rods. The question is I want to install a automatic transfer switch just after the 200 amp disconnect and the local inspector says that I would have to replace the 3 wire to the panel with a 4 wire. This installation was installed at least 15 years ago. The only problem that I see with this would be that the neutrals and grounds had been isolated and they should have been bonded at the main panel. There is no metal connections between the buildings. The inspector (it's a small country town) insist that if I put the transfer switch in I have to replace the wire even though he sees nothing wrong with the neutrals and grounds being separated in that main panel. Am I missing something?
Thanks for the help
Sparky1953
Thanks for the help
Sparky1953