Did you confirm (with clamp ammeter) that the return current from the other circuit is really coming back through that neutral into the breaker?
There might be another neutral wire running via a different route, or even a bootleg independent neutral over the EGC.
I have a copy of the same book, which makes me suspect hidden factors or a defective breaker.No I have not confirmed any measurements. Just did a visual confirmation when on site.
The circuit seems to be working fine.
This set up should not work (at least in my book)
Are you sure there are not actually 2 neutral conductors in the cable? 14/2/2 or 12/2/2?
What is this circuit feeding?
(AFCI) Bedroom and (Non afci) exhaust hood.
Don't ask me why this set up.
I'm placing all my chips on that one.a bootleg independent neutral over the EGC.
Just answering:Isnt this a violation anyway seeing that a mwbc sharing a neutral is to be on a common trip two pole breaker? just asking
An AFCI which includes a 30ma ground fault detector would have to have its own dedicated neutral for the hot wire it protects.yea I thought of that after I posted but still I pondered the functionality of the circuit w/ the AFCI forgive me if Im wrong, but does'nt the AFCI work on the theory of neutral current to the phase its operating on if so wouldn't the second (non afci breaker) have to be on the same phase in order to work without nuisance tripping. If this is so then the circuit would still be in violation. Im still in wonderment on the AFCIs. thanx
Can I get a high five?After troubleshooting, the NON afci was feeding a guest bathroom receptacle that apparently never had anything plugged in it. Hence the AFCI that was feeding the room had never tripped.
After I loaded the bathroom receptacle with my load bank, the AFCI tripped like a charm.