Strahan
Senior Member
- Location
- Watsontown, PA
I'm currently working up an estimate for a customer who has installed a tankless water heater and needs electric run to it. His main service panelboard is full. I want to istall a 100amp "sub-panel" in order to provide enough room for the water heater. I'm finding lots of reference to panels installed at separate buildings but not necessarily same building. I'm treating this as a feeder and the panel will not be very big circuit number wise. I know to keep the grounded conductor and EGC separated at the feeder panel, but should I also run a bonding wire to the water heater since this panel is feeding it? I'm pretty sure I do.
Also, does the feeder panel require a main OCPD? reading 408.36 I'm thinking as long as the panel is rated for 100amps and is less than 42circuits which it will be I don't need one. Before anyone talks about load study being done I have looked at what is currently there and his main panel now is a 200amp but very small in number of circuits. Instead of replacing the main panel with a bigger circuit one the homeowner is requesting a feeder panel be installed. He doesn't want to go through the hassle of dealing with replacing the main panel. Any help would be appreciated. Thanks!
Also, does the feeder panel require a main OCPD? reading 408.36 I'm thinking as long as the panel is rated for 100amps and is less than 42circuits which it will be I don't need one. Before anyone talks about load study being done I have looked at what is currently there and his main panel now is a 200amp but very small in number of circuits. Instead of replacing the main panel with a bigger circuit one the homeowner is requesting a feeder panel be installed. He doesn't want to go through the hassle of dealing with replacing the main panel. Any help would be appreciated. Thanks!