mshields
- Boston, MA
I've got a contractor who installed PVC conduit for the 24VDC lighting circuits within an MRI room.
He did this on the advice of the MRI technician in order to avoid installing Ferrous, Steel, EMT. He should have installed non-Ferris Aluminum conduit both because the circuit needs to be shielded (and that by the way is the big problem) BUT also because the mechanical protection of branch circuits serving patient care areas (that are part of the EES) may not be non-metallic.
To solve the shielding issue I'm considering allowing the contractor to copper tape the PVC conduit. I am left with the code issue. My question is, might there be a lieu pole here given that the branch circuit feeds a 24VDC power supply. Are the 24VDC conductors still a branch circuit? And if they are, does the fact that they are low voltage and either a Class 2 or Class 3 circuit, have any bearing?
Thanks,
Mike
Thanks,
Mike