domnic

Senior Member
Occupation
Electrical Contractor
I have four 150 watt hps lights installed on a building they pull 3.2 amps each with they came with no capacitors. the specifications on the transformer states if i use a 55uf cap the lights will pull 1.5 amps each. can i put one cap on the line to these lights to do the same thing if so what size cap for all four lights?
 
I have four 150 watt hps lights installed on a building they pull 3.2 amps each with they came with no capacitors. the specifications on the transformer states if i use a 55uf cap the lights will pull 1.5 amps each. can i put one cap on the line to these lights to do the same thing if so what size cap for all four lights?

Yup, caps across the incoming line will work. 55uF at something like 370 volts will work. Just make sure they are rated for HID fixtures.
 
Yup, caps across the incoming line will work. 55uF at something like 370 volts will work. Just make sure they are rated for HID fixtures.
Are you really saying that if each luminaire wants a 55uf cap you can put one 55uf cap on the line feeding four luminaires and get the same effect? Your answer appears that way.
 
150 hps

150 hps

You are saying if i have one lamp or ten lamps one 55uf cap will work for all lamps?
 
Are you really saying that if each luminaire wants a 55uf cap you can put one 55uf cap on the line feeding four luminaires and get the same effect? Your answer appears that way.


Incoming line to the fixture, which would be in the fixture itself. Not the feeder. Also notice the mention of HID rated capacitor.
 
150 hps

150 hps

THIS IS A HYPOTHETICAL QUESTION . WY CANT I USE ONE CAP ON THE LINE SIDE OF LAMPS FOR ALL LAMPS. HOW FAR AWAY CAN THE CAP BE FROM LAMPS?
 
THIS IS A HYPOTHETICAL QUESTION . WY CANT I USE ONE CAP ON THE LINE SIDE OF LAMPS FOR ALL LAMPS. HOW FAR AWAY CAN THE CAP BE FROM LAMPS?


One cap on the feeder would not produce enough leading current to cancel the reactive lagging current. Each cap is sized to cancel out most of the lagging current from the ballast.

If you did want to use on cap you can do that, but it would have to be much larger, and current would only go down at the point of attachment.


FWIW don't sweat the caps. Ive done the same :)
 
150 hps

150 hps

If i had four lamps at 55uf each can i use a 120uf on line side of the lamps to get the same PF.
 
150 HPS

150 HPS

If a 150 watt hps was installed on my home with no cap would it cost me more to run than one with a cap?
 
No
Residential electric meter registers Watts=volts x amps x power factor. The same reason power saving units sold don't really save money. They just like to show you how amperage goes down but don't show you power factor going up thus nullifying end result.
 
Last edited:
150 HPS

150 HPS

If I have a 150 hps light with 50% POWER FACTOR THE VOLTAGE AND AMPS ARE 50% OUT OF LINE WOULD BE 1/2 VOLTAGE AND 2 TIMES AMPS TO RUN THE LIGHT?
 
If I have a 150 hps light with 50% POWER FACTOR THE VOLTAGE AND AMPS ARE 50% OUT OF LINE WOULD BE 1/2 VOLTAGE AND 2 TIMES AMPS TO RUN THE LIGHT?
It does not work that way. Voltage and current are what you measure and voltage does not change. The phase angle between voltage and current changes, and the projection of the current vector onto the voltage axis gives the real power.
 
If I have a 150 hps light with 50% POWER FACTOR THE VOLTAGE AND AMPS ARE 50% OUT OF LINE WOULD BE 1/2 VOLTAGE AND 2 TIMES AMPS TO RUN THE LIGHT?
Volts applied is still same no matter what the PF is.

If your input amps is 3.2 amps and voltage is 120 then VA is 384. If PF is .50 then Watts is 192, VAR is 332.

To correct to .95 PF you need a capacitor with a 269 VAR (don't know right off how to convert that to microfarads). This would leave you still with 120 volts input and 192 watts, but VA will drop to 202, with remaining VAR of 63.

As far as where to place in the circuit, where do you want PF correction? This is light enough load that it really wouldn't have much impact on the branch circuit unless it was a really long run, then it would help with voltage drop because actual current is lower, and would lower line losses. put all four lights on one long run and your current goes up 4 times, but is reduced if correction is on load end.

Becomes a question of what are your concerns and what you may be trying to accomplish. Outside of line losses watts remains the same either way and that is what you are billed for unless you do have power factor penalties assessed to you.
 
150 HPS

150 HPS

So if i use a cap at each light i can use a smaller wire i will have about 1/2 the amp draw lets say ten lights on cap 32 amps with caps 16 amps?
 