hurk27
- Portage, Indiana NEC: 2008
What is the choke effect when it is carrying current from a lightning event?
I do agree that it is probably not an issue with normal AC current that is present at about any time.
Lightning is a high frequency high energy event, when you run a conductor through a ferrous metal race way it becomes a short circuit to high frequency AC current and can cause extremely high currents to build up in the raceway that can cause a fire, a choke in this sense is like a transformer with its secondary shorted, apply DC to the primary and nothing happens but apply AC and a higher lever of current tries to flow, many DC applications will use a 1:1 transformer with windings rated for the loads current, each side of the transformer is placed in series with each supply conductor, lets say you have an A winding and a B winding, A1 would be hooked to the supply + wire and B1 would be hooked to the supply - wire, the wires to the load will hook the same way A2 to the + to the load and B2 to the - to the load, any AC that tries to flow in this DC supply choke will be shorted out, choke come in many flavors from a simple couple turns around an iron core to very sophisticated designs that only allow it to pass frequency's below a design level or within a given range of frequency's, by bonding both ends of a raceway you eliminate the choking effect as the conductor and pipe become just one larger conductor.
Another way to think of it and why it got it's name is think of a garden hose, squeeze (choke) it down and it will restrict the water flow in a wire this will cause heat