mikewillnot
- Rochester, NY
- electrical contractor
I looked at a barn yesterday (several, actually), and they asked for a quote on some work. I've attached a seriously crude sketch of the distribution.
This is not a commercial agricultural operation. It's a family deal, an older couple with a small amount of livestock mainly as pets, including (1) goat, (1) horse, (?) chickens, (4-6) cows, and (1) pot-bellied pig named Wilbur. A donkey passed away the night before I got there, so he doesn't count. The barns are good sized, and quite roomy, I would think, for this quantity of animals. On a close look, the wiring is a nightmare.
Distribution, generally:
HOUSE breaker panel -> Barn A
underground, looks like URD or some kind of aluminum triplex, in EMT where visible, on double-pole 50-amp breaker in house panel
At building A, terminates in 6" PVC j-box on outside wall of A. no breakers in barn A or thereafter.
GFCI receptacle in additional box mounted on J-box.
Cable connected to GFCI load terminals feeds through wall to inside of A, and then feeds several lights, switches, and receptacles, all wired on 14ga UF.
Barn A -> Barn B
Same kind of feeder as from house to A, in EMT where visible.
Terminates at B in 6" PVC j-box on outside of building.
Cable connected to GFCI load terminals feeds through wall to inside of B, and there feeds several lights, switches, and receptacles, all wired on 14ga UF.
Barn A -> Henhouse
Additional cable connected at barn A j-box, when I got there connected to line side of GFCI, feeds to detached henhouse via 1/2" EMT barely buried and obviously in poor condition.
The GFCI receptacle on A had been damaged due to water. Replaced it, reconnected henhouse to GFCI load; tripped. Left henhouse disconnected.
I realize, and told them, that there's a whole lot of problems here, the worst being a whole lot of 14ga wire on a 50-amp breaker, using the ground for a neutral.
Told them
1) they need small outdoor breaker panel on barn A, instead of the j-box, with proper grounding, feeder configured for 120volts and an insulated neutral, and 15-amp breakers for each building, as all the "branch circuit" wiring was only rated for 15 amps.
2) there's a ground-fault on the henhouse line, either "underground" or in the henhouse, that has to be located and corrected. Also, the "underground" line needs to be underground.
I am completely open to any comments and/or suggestions. Please.
Barn A -> Barn B
Barn A -> Henhouse
Told them