Hi guys, can't seem to get the right answer from anyone on weather is permitted to feed a sub panel from another sub panel, some people say yes is ok others say no. who is right? I looked for the answer in the 2011 code book but couldn't find it.
Yes you can feed a sub panel from a sub panel and then you can feed another one from that one and another one from that one and another one from............................Hi guys, can't seem to get the right answer from anyone on weather is permitted to feed a sub panel from another sub panel,
Look at large facilities such as hospitals, there can be hundreds (maybe even thousands) of panelboards and they are not all fed from the MDP.
Unless you have local amendments or other specifications that 5% is just a suggestion in an informational note and not an NEC requirement. Depending on the load supplied maybe it is a good idea, other times it may not matter all that much.Yup. As long as your grounds remain isolated from neutral. Also consider your total voltage drop from from the main panel to the furthest branch outlet on the furthest sub panel. Should be within 5%.
Two huge differences in your example.I agree. There's a huge difference if the end of the line is an LED can light or a 10kw electric furnace![]()
Voltage drop to a motor - the motor will just draw more current - which of course will mean even more drop- but will still do the work as long as the drop isn't too much to create severe problems. More energy will be wasted, the motor will run hotter, but the user may not really notice any of this.
Even that is uncertain, if the motor is lightly loaded reducing voltage will reduce current.
There are energy saving devices that adjust the voltage supplied to loads like conveyors that spend a lot of time running under loaded.