I have never seen a module spec'ed that way. All that I have seen have a Voc number and a beta number for calculating corrected voltage for temperature.The cut sheet on the modules says the VOC can be plus or minus 10%, when calculating string voltage should I consider the possible 10% increase so as not to exceed the inverter max voltage input of 600 volts?
I've also seen people commit mistakes that exposed inverters to 800-900V for a short time until someone said "why isn't it turning on?" and fixed it. And I've yet to see an inverter get damaged that way.
The cut sheet on the modules says the VOC can be plus or minus 10%, when calculating string voltage should I consider the possible 10% increase so as not to exceed the inverter max voltage input of 600 volts?
PV module Voc does vary with irradiance, but not a lot:
View attachment 11398
The above is from a 2009 REC data sheet and is typical.
A PV module data sheet on the REC Solar website (www.recgroup.com) does show a tolerance that is missing on many data sheets:
"Analysed data demonstrates that 99.7% of panels produced have current and voltage tolerance of ?3% from nominal values."
These have all been interesting opinions but, no one has addressed the question from a code requirement approach. Do you really think the comments "it should never be an issue because I have never seen it happen." will hold up to an inspector?:blink:
Then why does there cut sheet say the Voc can be plus or minus 10%, seems like they have an internal conflict.
Then why does there cut sheet say the Voc can be plus or minus 10%, seems like they have an internal conflict.