430.62 refers to 430.52 to calculate the higher load, which refers you to Table 430.52. Per the conditions in the question 175% is used to calculate the largest motor. Look at the Exception in 43.52, and tell me what you think. From my understanding, it says you can use a higher size, rating or setting that does not exceed the next higher standard rating. So 50amps at 175% is 87.5 amps So I interpret 430.52 (Exception) as using a 90 amp rating and adding the other motors to this amount which is 174 amps. Since this is not a standard size per 430.52(Exception) then I can increase the size to the next standard size that does not exceed the next higher size, which is 175 amp OCPD. 1