Hypothetically
A manufacture is saying to wire their suana with 10 wire on a 30amp circuit.
The sauna is 6000 watts @240v.
I'm seeing 25 amps at 125% = 31.25
I'm seeing 80 % of 30 =24 amps not 25.
I'm thinking 8's on a 40 amp.
Am I right or wrong? If I'm right, because the manufacturer says 10's on a 30 am I wrong for not following the manufacturers directions?
Thank you