mporterf
- Athens, Da
Question....Can anyone tell me if the code allows for 20amp lighting circuit to feed a 15 and switch via #12 awg, then reduce the wire size down to #14 awg to feed the lighting load?
I am amazed at how often this question is asked. It is definitely non compliant to undersize the switch leg as that switchleg is part of the branch circuit. Art 240.4(D) will not allow it unless you install a 15 amp breaker
I once looked wayyy back to see if the practice was ever compliant and don't recall the result of my search , but it was allowed, by practice, in this area of GA and TN about 20 years ago and the practice died hard.I am amazed at how often this question is asked. It is definitely non compliant to undersize the switch leg as that switchleg is part of the branch circuit. Art 240.4(D) will not allow it unless you install a 15 amp breaker
Also true in my part of Georgia (northeast).I once looked wayyy back to see if the practice was ever compliant and don't recall the result of my search , but it was allowed, by practice, in this area of GA and TN about 20 years ago and the practice died hard.
Another factor in earlier times was #14 60?C conductors were rated 20A. Not sure when Article 240 requirements for small conductors came into existence.reduced conductor for switched legs was common here as well. There was no inspections in most single family dwellings in the area until about mid 1990's so nobody was correcting those that didn't know any better until that time.
Use of very high temp insulation "fixture wire" permanently attached to the fixture can be a big factorWhat's the article that allows us to use smaller gauge fixture whips?
Nvm found it. 410.117
Of course likely the other reason is how murky things would get out in the field if electricians were left to determine when #14 was allowable on a 20a circuit. Can you imagine trying to write a clear code section about that?