- Lockport, IL
- Retired Electrical Engineer
A load is not ?emergency? unless some governmental agency declares it to be so. One example is that building codes have declared egress lights to be emergency loads. The rules tell us that if utility power is lost, the egress lights must remain on for 90 minutes. Clearly, the intent is to give the occupants a safely illuminated path for exiting the building. Since your building?s occupants are not going to want to exit the building, you will need more than a simple battery backup for the egress lights. You will need the generator to be able to prevent the batteries from taking over the lighting load. Otherwise, the batteries will run down while the building is still occupied. Later, if the generator fails, at which point the occupants will have to leave, the egress lights won?t be available. I think you can accomplish this without having to designate the backup generator as serving emergency loads. I also doubt that there are any other emergency loads in the building that would require the generator to serve as their article 700 backup source. Bottom line, I think you can get by with one ATS, as long as battery systems serve as the official backup source for anything classified as an emergency load.