Multiple Motor Feeder

Status
Not open for further replies.

Hugh W

Member
Location
Mebane, NC
If you have one feeder supplying two motors one 10HP and 15HP @ 480V, so when determining the feeders you would multiply the largest motor by 1.25 and then add the other FLA for a total of 40.25A, since there is one conduit feed would you derate by .80 for more than three current carrying conductors in the raceway and figure the conductors for 50A?
 
I think OP means: two circuits, each supplying a single motor, in a same conduit. Then, according Table 310.15(B)(3)(a) for 4-6 conductors 0.8 it is the adjusting factor indeed.:roll:
 
I think OP means: two circuits, each supplying a single motor, in a same conduit. Then, according Table 310.15(B)(3)(a) for 4-6 conductors 0.8 it is the adjusting factor indeed.:roll:
Yet if that be the case, the rest of the post makes no sense. There is no 125% largest motor factoring plus FLA of others on a single motor circuit.
 