My understanding is that Arc Flash Risk Assessment is comprised of two components: hazard identification and likelihood of occurrence of that hazard.
The company I work for is paying a third party to calculate the incident energy value and arc flash boundary for all switchgear, panelboards, MCCs, etc. This is the hazard identification component. We still need to determine the likelihood of occurrence of those hazards.
Do we use 70E Annex F to determine the likelihood of occurrence? If so, can someone point me to information that explains, in detail, how to correctly use this annex? Any information that you?ve found helpful would be appreciated. I?ve searched online for a few hours only to find there aren?t many detailed examples on how to execute the procedure.
Also, 130.5 (C) (1) says, ?Arc-rated clothing and other PPE shall be used by the employee based on the incident energy exposure associated with the specific task.?
The calculations show an incident energy value at a particular place on the equipment, for example such as the load side of a main breaker on an MCC. It doesn?t account for any specific task. Is the PPE level related to the specific task and calculated incident energy?
Thanks
Thanks