I am installing single conductors for feeders in a ladder tray per section per 392.80 (A) (2) (D) and I am wanting to use table 310-15-B-17. Once I meet the requirements of 392.80 which for example will allow me use a parallel 4/0 instead of (3) sets of 500MCM's. I will need to terminate these conductors on a breaker in the switchboard and field disconnect. Per section 110-14-C, will I have to change this transition over to the 3 sets of 500MCM before terminating the breaker and disconnects per section 310-B-16. I do not want to splice all free air conductors prior to terminating the breakers if possible. I'm trying to determine the reason for 110-14-C?