It really only needs to be the size of the maximum unbalanced load it will see, though that may or may not be all that easy to determine. You would need to look at what circuits are supplied by the second bar and what maximum imbalanced load may be. If it is a case where only neutrals from breakers on that side of the panel attach to the bar on that side - you could easily have a lower maximum if all your straight 240 volt loads were landed on that side of the panel. If you really don't want to take any chances use same size of conductor as the feeder neutral - though you may need special adapter lugs or maybe a tap connector on the feeder conductor itself because of limited number of lugs that accept larger conductors.Good morning
I am converting a 200amp main panel to a sub panel. The ground bars are bonded to the panel . The neutrals were unbounded to the panel.
what size conductor is needed to connect the left neutral bar to the right neutral bar ?
Thank you
I would think that you would have to size it based on the panel main breaker and not the possible unbalanced load. I would always size it based on the main breaker or MLO rating, I believe this is how it was originally installed, doing it otherwise might be a violation of 110.3 (b)
The conductor in question is the neutral conductor of a feeder, just happens to only carry part of load of the entire feeder neutral. Feeder conductors are sized according to 215.2. Maximum possible unbalanced load on this conductor is the minimum ampacity required, but it must be no smaller then called for by 215.2(A)(2) which tells us it must be at least the size or the equipment grounding conductor even if the load is less - so for a 200 amp feeder 250.122 says 6 AWG copper - that means even if there is only maximum 20 amps of neutral load you still need a 6 AWG feeder neutral conductor.