gar
- Ann Arbor, Michigan
- EE
141227-2414 EST
A Lutron three wire dimmer, that is one that requires a neutral, has an approximate phase shift adjustment range for turn on of 45 degree (2 mS) to 150 degree (6.8 mS). This requires no load to operate. Based on a sample of one.
A highly inductive load will cause problems, and requires sufficently low shunt resistance across the load to correctly function.
You can run your own experiments with a scope for verification.