transman2
- Brooklet,Ga.
Is it legal by code to run service conductors from out door pad mount transformer to indoor service rated fire pump controller or would I need to install a outside disconnect on wall before entrance.
We have some fire pump gurus and hopefully one of them will provide an opinion, but as I see it that would be a violation of 695.6(A) and 230.6 unless the conduit within the building is encase in 2" of concrete or brick.PVC Conduit runs from POCO pad mount transformer underground to exterior wall and up wall with rigid and then through wall via a LB and then via emt to the service rated fire pump controller. Inside at a trough we paralleled the 3 phase to feed a service rated jockey pump controller. Is this this ok.
No GURU here but I will gladly chime in.PVC Conduit runs from POCO pad mount transformer underground to exterior wall and up wall with rigid and then through wall via a LB and then via emt to the service rated fire pump controller. Inside at a trough we paralleled the 3 phase to feed a service rated jockey pump controller. Is this this ok.