I"ve always heard rumors that multiple gfci outlets that are daisy chained together can interfere with each other causing lots of false trips and i've just believed it til today. Is this true, if so, why ? Or is it an another electrical urban myth ?
I haven't heard of any real problems with the practice.
Who told you there would be such a problem?
Multiple people over the years really. Many of them ol' time master electricians and other electricians. Generally, just showed up, put a new one in on first device, removed unneeded ones and went back to work. Got a call today same situation and started thinking about it, hence the thread
when you say daisy chained do you mean the load of the first GFI feeds the line of the second gfi ?
What would even be the point to that? I would think you either pigtail and use gfi's where needed or one gfi and feed thru to he other outlets.Tends to make communication easier when we use terms like line and load, rather than daisy-chain and downstream, doesn't it?
And I agree with you installing a gfci on the load side of a gfci can cause nuisance tripping.
fwiw, I've seen it more with Leviton than with Eagle or P&S, but that is an entirely subjective observation.
when you say daisy chained do you mean the load of the first GFI feeds the line of the second gfi ? If so yes there can be some nuisance triping pending on the trip curve of the gfi pending on device construction and manufacture. But if they are tapped to line side for each, there shouldn't be an issue
As long as he provided an access panel it would not be uncommon....I also saw it once at a whirlpool tub. Electrician couldn't find any gcfi device or breaker, so he put one under the tub.
Numnutz didn't realize somebody had fed the tub from the receptacle at the sink
As long as he provided an access panel it would not be uncommon....![]()
I guess he did not have a GFCI tester to check out his supply.Another bathroom.
I guess he did not have a GFCI tester to check out his supply.![]()
Yes, they went in line and out the load to each one. There were 5 total. There were 8 receptacles on that circuit as it ended up.