Multi-wire circuits and AFCI protection

Status
Not open for further replies.
Hey guys. My question is about Multi-wire branch circuits and AFCI protection. According to the 2014 NEC pretty much every 15 and 20 amp 120 volt branch circuit has to be AFCI protected. Is it possible to use 2 AFCI breakers for a Multi-wire circuit and tie their handles together or will the AFCI not work correctly in that configuration? Or do they make 2-pole breakers with AFCI protection? Thanks for any info you can give.

Dan
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
A double pole AFCI would be required for MWBCs and they are manufactured]
(example Siemens Q220AFCP.. "big box" price $85).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Ge has designed their afci so that you can use 2 sp afci breakers with a handle tie for a multiwire branch circuit.

ry%3D400
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Interesting ! Looks like the ole fart is behind the times AGAIN
 

jap

Senior Member
Occupation
Electrician
Ge has designed their afci so that you can use 2 sp afci breakers with a handle tie for a multiwire branch circuit.

ry%3D400

So what senses the fault on the on B phase breaker since the load neutral connected to the A phase breaker only ?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
So what senses the fault on the on B phase breaker since the load neutral connected to the A phase breaker only ?
The breaker on the B phase senses the fault.
Unlike a GFCI, the AFCI does not rely on matching signals on hot and neutral.
The sensitivity of the B breaker may be somewhat lower for line to neutral arcs, but a line to ground arc would not show an arc signature on the neutral anyway.

Now a line to neutral arc from the B phase might trip the A breaker too through the arc signature on the neutral.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Would 2 single pole AFCI breakers tired together work with that type of square D produc?

Dan


No-- GE's unit is made this way but I am unaware of any other manufacturer who has done that. I have heard that Seimens has taken the GFP out of their AFCI breakers but I don't know if they followed suit with GE.
 

kwired

Electron manager
Location
NE Nebraska
Would 2 single pole AFCI breakers tired together work with that type of square D produc?

Dan
Bottom line is if the breaker has any level of GFP it needs all ungrounded and grounded circuit conductors run through the breaker, anything that leaves via the GFP CT monitor must also return through the CT monitor or it will trip on ground fault. As mentioned GE is the only one that doesn't include GFP in their AFCI's and possibly Siemens.