mivey
It is a noticeable difference. For smaller wire (below the aught ranges) the impedance difference is less than a few percent (steel having higher X and lower R). From there to 500s or so it may be up to a 5-10% difference. Above that it seems to top out with steel having about a 20% higher impedance.I don't know how any VD calculator would alter its results, if you selected a different material for the conduit. I just believe that unless you are dealing with many hundreds of feet, or perhaps even thousands of feet, the influence of the conduit material would be too small to measure.
Not much change in the steel to aluminum resistance or impedance ratios but the kicker is the increase in the X/R ratio. That is significant because the steel run has an inductance about 20-25% higher than the aluminum (thus the 20% top-out for the bigger wire).
PS. And yes that included the conductor, CU I believe.