I will get more detail today so at the moment this is somewhat of a generic question.
Yesterday I saw some what appeared to be VFDs, most likely foreign due to a C-E rating and a 400v input power (@104 amps).
The secondary on each of the drives supplied (4) manual motor starters (IEC) that apparently provided OCP and a disconnecting means for individual motors.
Before I dig more deeply, is there any problem with this set up as far as the manual starters providing the OCP on the load side of the drive ? Secondly, there drives are connected to 480v.
On the surface it would appear to be a violation of 110.4, however, my guess is the 400v rating is based on 50Hz although it does not state. Is it a violation and/or unsafe to operate these drives with a 480v 60Hz input ?