marmathsen
- Seattle, Washington ...ish
- Electrical Contractor
Can I Install a 40A branch circuit for a heater in a dwelling?
Here's the situation:
In a single family dwelling we have a 6000 watt dual element infrared heater on a deck that is currently fed with 8 AWG conductors and a 40 amp circuit breaker. Article 424.3(a) states that a single heater can be any VA or wattage, but also states that two or more outlets shall not be fed by a circuit larger than 30A. Article 424.3(b) requires heating circuit conductors, panels and overcurrent protection to be rated at 125% of the load, but Article 210.20(a)exception permits sizing the panels and overcurrent protection at 100% if the equipment is rated for 100% operation.
My inspector first said that the conductors were too small. I responded saying that it is 8 AWG wire. He then said, that the switch being used to control the heater was too small. I responded saying that the 20A switch was listed for this use by the manufacturer (two switches each control 1 phase of each of the 3000 watt elements and should only be required to have a 15.625A rating). He asked for documentation proving that. I sent it, he escalated it to the lead Seattle inspector, the lead inspector called the manufacturer. The lead inspector eventually settled on the fact that he felt that the dual element heater is considered 2 outlets (I don't agree, do you?) and 424.3(A) limits the circuit to 30A.
So to summarize:
Can I have a 40A branch circuit feeding a 6000 watt heater in a residence?
-if not then-
Can I use a 100% rated circuit breaker and enclosure and install a 30A circuit breaker?
-also-
Are individual element connections on one heating appliance considered individual outlets, or is it one outlet that supplies one heating appliance?
So to summarize:
-if not then-
-also-