Shackled Designer
- Decatur, AL USA
Heya, Folks.
I have an industrial panel fed by 480V, 3-phase, delta without corner ground. A single-phase transformer is connected to one of the branches on this panel's supply circuit. If I read article 240 properly (NEC 2014), then it seems I need to protect each of the primary conductors to the transformer with a fuse, right? In other words, use two fuses, one per primary conductor, instead of just one. This is the conclusion I reach from 240.15 - A, which states:
Have I rightly understood? I simply wish to be certain I'm reading the code correctly.
I ask since most writing on this subject seems to address how much overcurrent protection is needed in terms of amp ratings, but not on the number of conductors to be protected.
Thinking a bit more about the issue, a lone fuse would protect the conductor from a phase-to-phase fault in the transformer, but a ground fault in the transformer could present a problem for both primary conductors.
Thanks for feedback. Discussion, critique, etc. is welcome.
Shak
A fuse or an overcurrent trip unit of a circuit breaker shall be connected in series with each ungrounded conductor.
Shak