roblsmith3
- Cary, NC USA
I'm trying my hand at a large (to me!) commercial project, 60.58kw to be exact. We are on the 2011 NEC code here in NC. We are using 5x SMA SunnyBoy 6000TL inverters, 1x 7000TL, and 2x 7700TL. The max output for the 6000s are 25A each; 7000 is 29.2A; and the 7700s are 32A each. My question is about how to combine everything into a solar subpanel. When I do my calculations, each inverter output will be on a 40A breaker. 8 inverters x 40A = 320 A total.
Am I correct in figuring that I need a 600A Solar SubPanel with a 350A MCB in the subpanel?
This would allow up to 370A of solar to be backfed on the busbar.
Now for the Main Utility AC disconnect.....would I use a 400A disconnect fused at 350A? If so that would mean a conductor size of 500 kcm correct?:blink::?
Any suggestions or verifying my calculations would be greatly appreciated. Thanks everyone!